Fulfilling Conductor Fill Requirements
June 10, 2015
When counting the number of conductors in a box, a conductor running through the box with an unbroken loop or coil not less than twice the minimum length required for free conductors shall be counted as _____ conductor(s).
a) one
b) two
c) three
d) four
The correct answer is: b) two
Article 314 covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures. As outlined in Sec. 314.16(B)(1), "Each conductor that originates outside the box and terminates or is spliced within the box shall be counted once, and each conductor that passes through the box without splice or termination shall be counted once. Each loop or coil of unbroken conductor not less than twice the minimum length required for free conductors in 300.14 shall be counted twice. The conductor fill shall be calculated using Table 314.16(B). A conductor, no part of which leaves the box, shall not be counted."
Mike Holt