NEC Requirements in Aircraft Hangars
May 15, 2018
Highlights of Art. 513 of the 2017 National Electrical Code.
Article 513 of the 2017 National Electrical Code (NEC) provides the requirements for aircraft hangars. Here are some highlights:
  • Any pit or depression below floor level is a Class I, Division 1 (or Zone 1) location [513.3(A)].
  • It matters were the aircraft are. For example, an area within 10 ft horizontally from aircraft power plants or fuel tanks is Class I, Division 1 (or Zone 1). And this area extends from the floor to 10 ft above the aircraft [513.3(C)].
  • Aircraft electrical systems must be de-energized when the aircraft is stored in the hangar and (whenever possible) when the aircraft is undergoing maintenance [513.10(A)(2)].
  • External power sources for charging aircraft must be at least 18 in. above the floor [513.10(C)(1)].
  • All 25V, 15A and 20A receptacles that may be used for maintenance and/or portable lighting must be GFCI-protected [513.12].
  • If it’s a non-current-carrying metal part, bond it [513.16(A)]. The goal is to eliminate dangerous differences of potential.
  • Use an approved means to maintain the continuity of the grounding (bonding) conductor between the fixed wiring system and the non-current carrying metal parts of pendant, luminaires, portable luminaires, and portable utilization equipment [513.16(B)(2)].