Article 517 of the National Electrical Code (NEC) provides the requirements for health care facilities. Here are some highlights:
  • The requirements apply even to portions of buildings [Sec. 517.1].
  • The NEC broadly defines “health care facility” to include more than hospitals. It’s any building (or portion of a building) or mobile enclosure for providing people with care such as dental, psychiatric, nursing, surgery, etc. [Sec. 517.2].
  • Branch circuits serving patient care areas must have an effective ground-fault current path; this means run the circuit in a metallic raceway, metal-armored cable, or metallic sheath assembly [Sec. 517.12(A)].
  • Article 517 emphasizes the equipment grounding conductor, because it serves a key safety role.
  • Receptacle requirements and other requirements vary by type of space. The type is defined by its usage. These are general care [Sec. 517.18], critical care [Sec. 517.19], and wet procedure [Sec. 517.20].
  • A major chunk of Art. 517 is devoted to the “essential electrical system” for these facilities. The system must be capable of supplying a limited amount of lighting and power service that’s considered essential for life and safety and for orderly cessation of procedures during a power interruption [Sec. 517.25].