Ecmweb 7422 5 21 15wwhlarge
What’s Wrong Here? Hint: Hide-and-Seek Surprise
May 21, 2015
Hint: Hide-and-seek surprise
Discovering what’s behind this metal wireway cover would surprise most electricians. Those are exposed foot lug connectors energized at 480V installed on insulators that are secured to plywood installed in the bottom of the wireway. This could quickly become a disaster for the unsuspecting electrician who opens this cover without knowing what lurks behind it.
Section 376.56(B)(4) does not permit power distribution blocks installed in metal wireways to have any uninsulated energized parts exposed within the wireway. I believe this installation violates the intent of that Code section.
The wire bending space required by Sec. 376.56(B)(3) is also questionable where the conductors enter the connectors. A few of those terminals seem a little too close to the back of the wireway.
In violation of Sec. 376.56(B)(5), several of the terminal blocks are obstructed by other conductors laying right on top of the terminals. This can make it very difficult to access the terminals.
The use of plywood leaves me wondering if it is fire-retardant, or is it combustible? If the plywood is combustible that could be a real problem if there were a short circuit or an accidental ground fault in the wireway and some sparks were to ignite the plywood. A 4th of July type fireworks show would begin shortly thereafter. And, of course, there is always Sec. 110.12, which requires neat and workmanlike installations. I am not so sure that has happened here.
Russ LeBlanc | Owner
