Ecmweb 4858 406ecm15fig1
June 1, 2004
Hint: This AC supply is located in a wet location under an outdoor lift at a paper printing plant.
Shawn Hutchinson, a journeyman wireman with IBEW Local Union 640 in Phoenix, submitted this response to the photo in the June issue. “This fitting won't prevent moisture from entering or accumulating within the box, conduit body, or fitting as noted in 314.15(A),” he wrote. “In addition, conductors must be protected from abrasion as noted in 314.17. And if using electrical metallic tubing (EMT) as the equipment grounding conductor, the fitting must be made tight as noted in 250.120(A).”
Robert Weber, P.E., vice president of engineering, S.L. King & Associates, Inc., Atlanta, submitted this comment. “This electrical box is not suitable for installation in a wet location,” he wrote. “In addition, note the non-continuity of conduit, lack of proper support, exposed wiring, and lack of bushing. The broken bottle can also be cited as an OSHA violation.”
In addition to noting a violation of 314.15(A), Greg Sparks, electrical engineer, Portland International Airport, Portland, Ore., cited a violation of 358.10(B), which states “Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosion influences where protected by corrosion protection and judged suitable for the condition.”
Joe Tedesco