Ecmweb 13266 Nec Logo 0
NEC Rules for Industrial Machinery
June 18, 2019
How does Article 670 definite this type of equipment?
Article 670 provides the requirements for this equipment. But what exactly is it? An industrial machine is a power-driven machine that is:
  • Not portable by hand when working.
  • Used to process material by any of several specified means, including cutting and forming.
Industrial machinery also can include associated equipment used to transfer material or tooling.
The control equipment enclosure or the machine itself must bear a nameplate that provides the five types of information specified in Sec. 670.3(A)(1) through (5). For example, it must tell you the electrical diagram number(s) or the number of the index to the electrical drawings. Check the industrial equipment nameplates in your facility; do these reference drawings? If not, you have some updates to do for your facility to be NEC-compliant.
The supply conductors must have an ampacity of at least 125% of the full-load current rating of all resistance heating loads plus 125% of the full-load current rating of the highest rated motor plus the sum of the full-load current ratings of all other connected motors and apparatus [Sec. 670.4].
Strut Corrosion Guide
