Code Quiz: Installation of Fire-Resistive Cable Systems
Feb. 26, 2015
NEC guidelines for installing fire-resistive systems in a raceway
Where a fire-resistive system is listed to be installed in a raceway, the raceway enclosing the system is permitted to be which one of the following?
A)  rigid metal conduit
B)  intermediate metal conduit
C)  metal-clad cable
D)  a raceway that is listed as part of a fire-resistive system
Find the Answer
Answer: D
As noted in Sec. 728.5(C) of the 2014 NEC, where a fire-resistive system is listed to be installed in a raceway, the raceway enclosing the system shall be listed as part of a fire-resistive system. This also includes any couplings and connectors.