Ecmweb 24750 X Ray Results
NEC Rules for X-Ray Equipment
May 21, 2019
Generating X-rays requires high voltage, and Art. 660 requirements mostly address that hazard.
Article 660 in the 2017 National Electrical Code (NEC) provides the requirements for X-ray equipment. Exposure concerns have greatly diminished with the widespread adoption of digital X-ray machines, which produce much less radiation than their older film counterparts. So, the beam is less of a problem than it used to be. But Art. 660 is not about the beam [Sec. 660.1]. Generating X-rays still requires high voltage, and the Art. 660 requirements mostly address that hazard.
Some highlights from this section of the Code include:
  • All high-voltage parts must be mounted within grounded (bonded) enclosures [Sec. 660.47(A)].
  • The disconnecting means must have adequate capacity for at least 50% of the input required for the momentary rating, or 100% of the input required for the long-time rating, whichever is greater [Sec. 660.5].
  • The ampacity of the branch circuit conductors must meet that same 50/100 requirement [Sec. 660.6(A)].
  • Feeder conductors supplying two or more X-ray branch circuits must comply with Sec. 660.6(B).
  • Low-voltage cables that connect to oil-filled units that aren’t completely sealed must be of the oil-resistant type [Sec. 660.47(B)].
  • Non-current-carrying metal parts must be grounded (bonded) per Art. 250 [Sec. 660.47(C)].
Strut Comparison Chart
