Hint: As the main bonding jumper (the green screw) in this load side subpanel shows, the ends don't always justify the means.

How well do you know the Code? Think you can spot violations the original installer either ignored or couldn't identify? Here's your chance to moonlight as an electrical inspector and second-guess someone else's work from the safety of your living room or office. Joe Tedesco, who has a knack for finding shoddy electrical work, did the dirty work and found this mess. Now it's your turn to identify the violation.

Find the Answer

Robert O'Brien, project manager, Riggs Distler & Co., Inc. of Sharon Hill, Pa., pointed out that if this is a subpanel, then the green bonding screw in the neutral bar violates 250.24(A)(1), which notes that the service must be grounded at an accessible location up to the bus where the neutral is connected. This subpanel is located well past that point. Also, 250.24(A)(5) prohibits the grounding of the grounded conductor on the load side of the service disconnect, except as otherwise allowed in this Article. The subpanel is located on the load side of the service disconnect. However, if this were a separately derived system and this were the ground connection to the secondary grounded conductor, then the separate equipment grounding terminal bar would be a violation.

James Williams, president, Ace Electric of Shelby, Kings Mountain, N.C., noted other violations. The equipment grounding conductor and the grounded conductor (neutral) must be separate from each other in a subpanel. Use of the green screw violates the requirements of 408.20. Verification of 300.4(F) must also be ensured for the insulated bushing for the chase nipple.

John McEldowney, regional electrical inspection supervisor, New Jersey Department of Transportation, Trenton, N.J., noted the neutral terminal bars, located on each side of the enclosure, should be electrically bonded. His concern arose when he saw more than two green equipment grounding conductors terminated under several of the terminal screws, which is a violation of 110.3(B).

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.