Ecmweb 6277 4 24 14wwhpromo
What’s Wrong Here? Hint: Flimsy Limbs
April 24, 2014
Hint: Flimsy limbs
The only support provided for this 4-in. octagonal box is the ½ in. electrical metallic tubing (EMT) and the 3/8 in. flexible metallic conduit (FMC) connected to it. This is a direct violation of Sec. 314.23 of the 2014 NEC, which requires boxes to be secured with any of the provisions in Sec. 314.23(A) through (H). The only one of those sections that is even remotely close to being applicable to this installation is 314.23(E). This section of the Code requires the enclosure to have threaded entries or hubs and to have two or more conduits threaded wrench tight into the enclosure or hubs for proper support. If both of the conduits enter the same side of the enclosure, they should be secured within 3 ft of the enclosure or within 18 in. of the enclosure. Unfortunately, none of those requirements has been met.
The bottom line is EMT or FMC simply cannot be used to support a box. The Exception in 314.23(E) does, however, permit a conduit body to be supported by EMT. Using a support brace or securely mounting the box to the building or another surface would have been better than just sticking the box on the end of the EMT. I also question whether there is an equipment grounding conductor (EGC) installed in the FMC as required by Sec. 250.118(5)(d) when flexibility is needed.
Russ LeBlanc | Owner