Ecmweb 7225 Nec Whats Wrong Here 0315 Pr
What's Wrong Here? Hint: Fixture Flop
March 18, 2015
Hint: Fixture flop
January Winners
Our winners this month were: Bill Gallus, a retired electrical engineer from Johnstown, Pa.; Michael J. Gillean, the owner of Sonoma Valley Electric, Sonoma, Calif.; and John Osowski with Triple E Electric of Bedford, Ohio. Each of them was able to correctly identify the Code violations found in this poor excuse for a device box.
This installation makes “real” electricians cringe. Section 300.15 requires a box to be installed where NM cable has an outlet, switch, conductor splice point, or termination point. These wires were just stuffed into the wall cavity with no protection. Section 406.5 requires receptacles to be installed in identified boxes or assemblies. This low-voltage “ring” does not meet the definition of a box. It is intended to be used for low-energy Class 2 circuits, or communication-type circuits, and should not have been used to secure this receptacle to the wall. Using it in this manner violates the rules of Sec. 110.3(B). In addition, Sec. 334.15(B) requires protection for the NM cable where it passes through the floor. The cable could have been protected by enclosing it in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80-type PVC conduit, RTRC-XW conduit, or other approved means extending at least 6 in. above the floor.
Russ LeBlanc | Owner