Ecmweb 7562 7 9 15wwhlarge
What’s Wrong Here? Hint: Broken Pipe Dream
July 9, 2015
Hint: Broken pipe dream
This is an example of what happens when you try to use PVC pipes as the only means to support a box. Inevitably, the pipes will break, and the box will end up just flopping around. This now leaves the cables exposed and susceptible to physical damage. Damaged cables can greatly increase the shock hazard level.
Section 352.12(B) prohibits PVC pipe from being used to support luminaires or equipment other than conduit bodies as described in Sec. 352.10(H). Boxes are not conduit bodies and cannot be supported by the PVC pipe.
Section 314.23(E) permits rigid metal conduit (RMC) or intermediate metal conduit (IMC) to be used as a means of support for enclosures not greater than 100 cu. in. where two conduits are threaded wrenchtight into the enclosure and the conduits are supported within 3 ft of the enclosure, or within 18 in. of the enclosure where all the pipes enter the enclosure on the same side.
Russ LeBlanc | Owner