Ecmweb 3009 810ecmicpic1

Illustrated Catastrophes

Oct. 1, 2008
As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious safety questions. All references are based on the 2008 NEC. ABORT LIFTOFF! John M. Batavich of Stewart Engineering Consultants in Sarasota, Fla., found this lift station

As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious safety questions.

All references are based on the 2008 NEC.

ABORT LIFTOFF!

John M. Batavich of Stewart Engineering Consultants in Sarasota, Fla., found this lift station equipment at a project site he visited recently. “Although the luminaire mounted to the control panel appears to be listed for wet locations, the incandescent lampholder adjacent to the fence beside it is not,” says Batavich. “This control panel is located outdoors, and the ENT is exposed to direct sunlight. According to my interpretation, the installation is subject to physical damage. Type NM cabling appears to have been used for the incandescent lampholder, and is also serving as its sole means of support.”

The use of electrical nonmetallic tubing (ENT) is restricted in many locations. For example, it is not to be used in any hazardous (classified) location, except as permitted by other articles in the Code, or in exposed locations, except as permitted by 362.10(1), 362.10(5), and 362.10(7). It also cannot be used where exposed to the direct rays of the sun, unless identified as sunlight resistant, or where subject to physical damage. See 362.12 for a full list of restrictions. In addition, there are restrictions on the use of nonmetallic sheathed cable (334.12). This type of cable cannot be used in wet or damp locations.

WHAT LURKS ABOVE THE CEILING?

“Joe, here are some nice pictures on how not to hang pendant fixtures over tables in a restaurant,” says Fred Cocks, an electrical inspector with Commonwealth Electrical Inspection Service, Inc., Monroe, N.Y.

The space above this drop ceiling reveals a pretty scary and dangerous situation. The wiring method lacks proper support, there are missing covers on the handy boxes, and the fittings that are present aren't of the proper type. The list of Code requirements violated in this particular location are too numerous to list here. However, the list would begin with rules in Articles 300, 334, and 410.

Found a Code Violation? E-mail your photos (no cell phone images, please) to Joe Tedesco at [email protected]

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

Considerations for Direct Burial Conduit

Installation type plays a key role in the type of conduit selected for electrical systems in industrial construction projects. Above ground, below ground, direct buried, encased...

Electrical Conduit Comparison Chart

CHAMPION FIBERGLASS electrical conduit is a lightweight, durable option that provides lasting savings when compared to other materials. Compare electrical conduit types including...