Surge-Protective Device Conductor Length
The requirements for surge-protective devices (SPDs), 1kV or less, are outlined in Art. 285 of the 2011 NEC.
The conductors used to connect the surge-protective device to ground shall not be any longer than _____ and shall avoid unnecessary bends.
a) 6 inches
b) 12 inches
c) 18 inches
d) necessary
The correct answer is: d) necessary
The requirements for surge-protective devices (SPDs), 1kV or less, are outlined in Art. 285 of the 2011 NEC. As noted in Sec. 285.12, "The conductors used to connect the SPD (surge arrester or TVSS) to the line or bus and to ground shall not be any longer than necessary and shall avoid unnecessary bends."