Sizing Equipment Grounding Conductors for Motor Circuits
Section 250.122 of the 2011 NEC spells out the requirements for sizing equipment grounding conductors.
Equipment grounding conductors for motor branch circuits shall be sized in accordance with Table 250.122, based on the rating of the _____ device.
a) motor overload
b) motor over-temperature
c) branch circuit short-circuit and ground-fault protective
d) feeder overcurrent protection
The correct answer is: c) branch circuit short-circuit and ground-fault protective
Section 250.122 of the 2011 NEC spells out the requirements for sizing equipment grounding conductors. Equipment grounding conductors for motor circuits shall be sized in accordance with 250.122(D)(1) or (D)(2). As noted in 250.122(D)(1), "The equipment grounding conductor size shall not be smaller than determined by 250.122(A) based on the rating of the branch-circuit short-circuit and ground fault protective device."