Location of a Feeder Disconnect
The rules for locating a disconnect in a building are outlined in Sec. 225.32 of the 2011 NEC.
May 29, 2014
The disconnecting means for a building supplied by a feeder shall be installed at a(n) _____ location.
a) accessible
b) readily accessible
c) outdoor
d) indoor
The correct answer is: b) readily accessible
As noted in Sec. 225.32 of the 2011 NEC, "The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized."