Motor Terminal Torque Requirements
Article 430 covers the requirements for motors, motor circuits and controllers.
Torque requirements for motor control circuit device terminals shall be a minimum of _____ lb-in. (unless otherwise identified) for screw-type pressure terminals used for 14 AWG and smaller copper conductors.
a) 7
b) 9
c) 10
d) 15
The correct answer is: a) 7
Article 430 covers the requirements for motors, motor circuits and controllers. Motor terminal requirements can be found in Sec. 430.9. As per 430.9(C), "Control circuit devices with screw-type pressure terminals used with 14 AWG or smaller copper conductors shall be torqued to a minimum of 7 lb-in. unless identified for a different torque value.
Mike Holt
Mike Holt