Selection of Ampacity
Section 310.15 outlines the requirements for the ampacities of conductors rated between 0V and 2,000V.
The ampacity of a conductor can be different along the length of the conductor. The higher ampacity can be used beyond the point of transition for a distance of no more than ____ ft, or no more than ____% of the circuit length figured at the higher ampacity, whichever is less.
a) 10, 10
b) 10, 20
c) 15, 15
d) 20, 10
The correct answer is: a) 10, 10
Section 310.15 outlines the requirements for the ampacities of conductors rated between 0V and 2,000V. As noted in 310.15(A)(2), "Where more than one ampacity applies for a given circuit length, the lowest value shall be used." However, an exception notes: "Where two different ampacities apply to adjacent portions of a circuit, the higher ampacity shall be permitted to be used beyond the point of transition, a distance equal to 10 ft or 10% of the circuit length figured at the higher ampacity, whichever is less."