Ampacity Requirements of Armored Cable
Article 320 covers the use, installation and construction specifications for armored cable.
Type AC cable installed in thermal insulation shall have conductors that are rated at 90°C. The ampacity of the cable in this application shall not exceed that of a ______ rated conductor.
a) 60°C
b) 75°C
c) 90°C
d) none of the above
The correct answer is: a) 60°C
Article 320 covers the use, installation and construction specifications for armored cable. As noted in Sec. 320.80(A), "Armored cable installed in thermal insulation shall have conductors rated at 90°C. The ampacity of cable installed in these applications shall not exceed that of 60°C rated conductor. The 90°C rating shall be permitted to be used for ampacity adjustment and correction calculations; however, the ampacity shall not exceed that of a 60°C rated conductor.
Mike Holt
Mike Holt