Electrical Troubleshooting Quiz — June 2, 2020

Why does the new replacement breaker keep tripping?

During the last maintenance shutdown, your electrical testing firm identified an old 800A breaker as needing to be replaced. Among other things, it would not trip while under test.

The breaker supplies 480V to several branch circuit transformers. None of the loads are critical, so it was possible to schedule a mini-shutdown to replace the breaker.

There were no nuisance trips with the old breaker, but that is not the case with this one. Production is upset because you “replaced a good breaker with a bad one”. An electrician hung an inductive current clamp on the load side of the new breaker and read only 635A. What other tests should you perform, and what issues should you investigate?

First, find out if this is the correct type of breaker. Is it an instantaneous trip breaker when the application calls for an inverse time breaker? Are large motors starting across the line?

What about the settings on the breaker? It may be just one setting that is causing the problem. For example, you can adjust Continuous Amps to as low as 20% of the breaker’s rating. If you set the Continuous Amps for 80%, then the breaker would trip at 640A. The electrician measured 635A, so not much load change is needed for a trip. You could look at the setting of the old breaker, but was it correct? Determine the calculated load by the same process used in the NEC, Annex D3(a).

It would be good to use that clamp with a DMM that has a min/max recording feature, so you can see how high the actual load goes over a 24-hr period.

About the Author

Mark Lamendola

Mark Lamendola

Mark is an expert in maintenance management, having racked up an impressive track record during his time working in the field. He also has extensive knowledge of, and practical expertise with, the National Electrical Code (NEC). Through his consulting business, he provides articles and training materials on electrical topics, specializing in making difficult subjects easy to understand and focusing on the practical aspects of electrical work.

Prior to starting his own business, Mark served as the Technical Editor on EC&M for six years, worked three years in nuclear maintenance, six years as a contract project engineer/project manager, three years as a systems engineer, and three years in plant maintenance management.

Mark earned an AAS degree from Rock Valley College, a BSEET from Columbia Pacific University, and an MBA from Lake Erie College. He’s also completed several related certifications over the years and even was formerly licensed as a Master Electrician. He is a Senior Member of the IEEE and past Chairman of the Kansas City Chapters of both the IEEE and the IEEE Computer Society. Mark also served as the program director for, a board member of, and webmaster of, the Midwest Chapter of the 7x24 Exchange. He has also held memberships with the following organizations: NETA, NFPA, International Association of Webmasters, and Institute of Certified Professional Managers.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!