More Code Catastrophes As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious electrical safety questions. Dock Lighting System The electrical circuit supplying the light pole on this dock set up a rather unique installation.

More Code Catastrophes

As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious electrical safety questions.

Dock Lighting System

The electrical circuit supplying the light pole on this dock set up a rather unique installation. First, the electrical conduit served as a fence or railing for pedestrians. In addition to the missing covers on the conduit bodies, which leave exposed live wires accessible to the general public, there were exposed conductors at the top of the pole. In the close-up photo, you can see the cable isn't designed for this use. To top it all off, the equipment-grounding conductor is also missing. Per 410.15, metal poles are permitted to support luminaires and serve as a raceway to enclose supply conductors, provided the pole has a hand hole not less than 2 in. × 4 in. with a raintight cover to provide access to the supply terminations within the pole or pole base.

Required Horizontal Clearances

Although this switch can be opened to make repairs and replace fuses, access to the equipment looks like it may have been in violation of Code rules in effect 35 years ago (when it appears to have been installed). A check of the 1965 Code, Sec. 110-16(a) covering horizontal clearances for 0V to 150V to ground, shows that conditions 1 and 2 required 2½ ft, and condition 3 required 3 ft. When this equipment is eventually replaced, the AHJ can consider acceptance of the installation in accordance with 90.4.

Living on the Edge, or Should We Say Roof

This violation can be found in an alley behind a major shopping center in the Midwest. When this electrical metallic tubing (EMT) was first installed several years ago, it was supported by the straps located on the lower edge of the fascia board. However, those straps no longer serve their purpose. As such, the threadless coupling has pulled apart and left a break in the continuity of the EMT, violating the grounding rules in Art. 250. Use of this raceway as a support method for cables or nonelectrical equipment also violates 300.11(B), where raceways are allowed as a means of support for other raceways, cables, or nonelectrical equipment under specific conditions not present here. So how did the threadless coupling come apart? It didn't help that street people living on the roof of this building used the EMT as a pull bar when accessing the roof.

Open Air Panel

One of my students, an electrical engineer with Honda Corp. in California, sent me this picture. He and his new wife found this open air panel in a villa while visiting a foreign country on their honeymoon. I'm sure we all agree it doesn't meet the requirements of 110.2. Panelboards are required to be installed in cabinets and comply with Arts. 312 and 408.

Now you can send Code Violations Illustrated stories and photos directly to Joe Tedesco at:

Joe Tedesco
350 North Street
Boston, MA 02113
or e-mail:
[email protected]

If you mail pictures, please include the story, location, and some information about yourself — and please do not write on the front or back of your photo. Please send all digital images in JPEG format. You can send photos while visiting Joe's Web site at: www.joetedesco.com

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.