    Note: The following Code references are from the 2002 NEC. Q. If it's not possible to locate the maintenance disconnect 5 feet from the equipment, could it be located within the hot tub assembly behind closed panels? A. No, the hot tub maintenance disconnect (680.12) must be located not less than 5 feet horizontally from the inside walls of an outdoor spa or hot tub, unless separated by a solid fence,
    Dec. 1, 2004
    3 min read
    Image

    Note: The following Code references are from the 2002 NEC.

    Q. If it's not possible to locate the maintenance disconnect 5 feet from the equipment, could it be located within the hot tub assembly behind closed panels?

    A.No, the hot tub maintenance disconnect (680.12) must be located not less than 5 feet horizontally from the inside walls of an outdoor spa or hot tub, unless separated by a solid fence, wall, or other permanent barrier [680.22(C)].

    In other than a “single-family dwelling,” a clearly labeled emergency spa or hot tub water recirculation and jet system shutoff must be provided. It must be readily accessible to the users and located not less than 5 feet away, but adjacent to and within sight of the spa or hot tub (680.41) (Figure at right).

    The emergency shutoff is meant to protect users. Deaths and injuries have occurred in less than 3 feet of water when individuals became stuck to the water intake opening. This requirement applies to spas and hot tubs installed indoors as well as outdoors.

    Q. I have a wall switch that's no longer needed. I'd like to remove the switch, cap the wires, and replace the switch plate with a blank one. Is this OK or must I remove the abandoned wires?

    A. The NEC doesn't require the removal of abandoned power and lighting conductors, just abandoned low-voltage and limited wiring. It's a good idea to disconnect the unused wires from their power source, but this isn't a Code requirement.

    Q. I have a cord-and-plug connected outdoor spa/hot tub motor that uses a GFCI-protected cord. The attachment plug is rated 15A and not of the twist-lock type. Where can I locate the receptacle?

    A. Outdoor spas must be wired in accordance with the same requirements as a permanently installed pool (680.42). Since the receptacle for the spa or hot tub will be of the non-twist lock type, the receptacle must be located not less than 10 feet from the inside walls of the outdoor spa or hot tub [680.22(A)(1)].

    Note: All 15A and 20A, 125V receptacles located within 20 feet of the spa or hot tub must be GFCI-protected [680.22(A)(5)], and all 15A and 20A, 125V receptacles located outdoors of a dwelling unit must be GFCI-protected [210.8(A)(1)].

    Q. Is there a section in the Code that restricts the use of extension cords?

    A. No. The NEC is an installation standard, not a product standard. However, listed extension cords should be used in accordance with the listed instructions, but this isn't a Code requirement. According to UL's Web site, extension cords aren't intended to be used as a substitute for the fixed wiring of a structure. So basically, an extension cord is only for temporary usage.

    Q. I'm working on a job where a drinking water fountain is proposed to be installed within 1 foot of a transformer. Is there a Code rule that governs the necessary clearance between the drinking fountain and the transformer?

    A. Yes. According to 110.26, you must provide sufficient step-back working space from energized parts, measured from the enclosure front, that are no less than the distances shown in Table 110.26(A)(1). Assuming this is a 480V to 208V transformer, the minimum step-back working space according to this table is 3.5 feet. The water fountain/cooler can be located right next to the transformer sides as long as the transformer ventilating openings aren't blocked (450.9).

    About the Author

    Mike Holt

    Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

    Voice your opinion!

    To join the conversation, and become an exclusive member of EC&M, create an account today!

    Sponsored Recommendations

    Sign up for EC&M Newsletters
    Get the latest news and updates.

    Latest from content

    © Sigoisette | Dreamstime.com
    Best Of 2021 Code Quizzes
    Here are the 10 quizzes that readers enjoyed the most last year.
    © Romolo Tavani | Dreamstime.com
    The Top Photo Galleries For 2021
    Check it out and see what content your fellow readers found the most interesting.
    Code Watch 1
    Think you know how this installation violates the NEC?

    Sponsored