• Code Quiz: Ground Rod Resistance Readings
    Test your Code knowledge regarding ground rod resistance readings. Does the NEC specify the maximum resistance of a ground rod?
    Dec. 2, 2021
    Question: Does the NEC specify the maximum resistance of a ground rod?
    See answer below.
    Answer: Yes and no
    Explanation: Section 250.53(A)(2) requires that a single ground rod be supplemented by another electrode. An exception allows a single rod if the resistance of this rod is 25 ohms or less. Many installers interpret this wording to mean they’re required to get a reading of 25 ohms or less on the ground rod. However, there is no NEC requirement for a specific resistance of the grounding electrode system. If you have more than one electrode the 25 ohms reading does not apply. In fact, you do not even need to test the resistance of the system. Note: Many specifications on a project do have resistance requirements for grounding electrodes that must be met.
    John Lupacchino is a senior design engineer with Gaylor Electric, Inc., in Noblesville, Ind. and serves as an alternate on NEC Code-Making Panel No. 3. He is currently licensed in more than 80 jurisdictions. He can be reached at [email protected].
    John Lupacchino
    Senior Design Engineer
