Code Q&A: Motor Protection
NEC requirements for protecting motors from short circuits, ground faults, and overload
Feb. 4, 2016
Q. What is the Code requirement for protecting a motor from short circuit, ground fault, and overload with a single device?
A. A motor can be protected against overload as well as short circuit and ground fault by a single overcurrent device sized to the overload requirements contained in Sec. 430.32 [430.55].
For example, let’s say you have a 5-hp, 230V, single-phase motor with a service factor of 1.15 and a nameplate current rating of 28A. As noted in Sec. 430.32(A)(1), motors rated more than 1 hp with a service factor of 1.15 or greater shall be selected to trip or shall be rated at no more than 125% of the motor nameplate full-load current rating.
Therefore, the fuse rating is calculated as follows: 28A x 1.25 = 35A.
Mike Holt
Mike Holt
