If you’re working with 800A or less, don’t worry if an OCPD rated at 700A won’t accommodate your loads, but one rated at 800A exceeds the ampacity of your conductors [240.4(B)].

Suppose your calculated load is 720A and the ampacity of the conductors being protected is 780A. Now look at this excerpt from the standard breaker sizes listed in Sec. 240.6 of the 2014 NEC: “...500A, 600A, 700A, 800A, 1000A....” Do you see the problem, here?

An OCPD rated at 700A won’t accommodate your loads, but one rated at 800A has a rating that exceeds the ampacity of your conductors.

But if you’re working with 800A or less, you don’t need to worry about this [240.4(B)]. You can use the next higher standard OCPD, if you meet these three conditions:

1) The conductors being protected aren’t part of a branch circuit supplying more than one receptacle for cord-and-plug connected portable loads (check this receptacle issue carefully, if working with a branch circuit).

2) There’s not a standard-size OCPD at that rating.

3) The next higher standard rating OCPD is less than 800A.

If you can’t meet those conditions, you’ll need to use larger conductors or move some loads to another circuit.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.