N-sky/iStock/Thinkstock
Ecmweb 8491 Branch Circuit

Protecting Ungrounded Conductors

Oct. 11, 2016
There’s a pretty big twist if you’re providing protection to motor circuits.

A fuse or the overcurrent trip unit of a circuit breaker must be connected in series with each ungrounded conductor [NEC Sec. 240.15(A)]. Also, the breaker must open all ungrounded conductors of the circuit both manually and automatically [240.15(B)]. There’s a pretty big twist to this, however, if you’re providing protection to motor circuits (see Parts III, IV, V, and XI of Art. 430).

For the ungrounded conductors of a:

1) Multiwire branch circuit that serves only single-phase line-to-neutral loads, you can use individual single-pole breakers with identified handle ties [240.15(B)(1)].

2) Line-to-line connected load on a single-phase circuit, you can use individual single-pole breakers rated 120/240V with identified handle ties [240.15(B)(2)].

3) 4-wire, 3-phase (or 5-wire, 2-phase) system, you can use individual single-pole breakers rated 120/240V with identified handle ties [240.15(B)(3]. Grounded neutral is required; voltage to ground can’t exceed 120V.

4) Line-to-line connected load on a 3-wire, DC circuit, you can use individual single-pole breakers rated 125/250V with identified handle ties [240.15(B)(4)]. Grounded neutral is required; voltage to ground can’t exceed 125V.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

Electrical Conduit Comparison Chart

CHAMPION FIBERGLASS electrical conduit is a lightweight, durable option that provides lasting savings when compared to other materials. Compare electrical conduit types including...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...