There are four exceptions to this rule [240.24(A)(10) through (4)].

The National Electrical Code (NEC) has very specific rules for the location of overcurrent protection devices (OCPDs). First, they must be readily accessible [240.24(A)]. There’s a height requirement that comes with that. The center of the grip of the operating handle (when in its highest position) can’t be more than 6 ft – 7 in. above the floor or work platform. There are four exceptions to this rule [240.24(A)(10) through (4). Do you know what they are?

If the application is an occupancy, each occupant must have ready access to all OCPDs protecting the conductors supplying that occupant’s occupancy [240.24(B)]. But two exceptions apply if electric service, continual supervision, and maintenance are provided by the building management:

  1. Service and feeder OCPDs don’t have to be accessible [240.21(B)(1)].
  2. Branch circuit OCPDs don’t have to be accessible if those circuits supply guest rooms or guest suites [240.21(B)(2)].

Locate the OCPDs where they won’t be exposed to physical damage [240.22(C)]. If such a location isn’t available, you may have to create one by, for example, installing bollards.

In addition, you can’t install them near easily ignitible material [240.22(D)] or in a bathroom [240.22(D)].

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.