Electrical Troubleshooting Quiz — Feb. 4, 2020
Last summer, the air conditioning at a manufacturing plant could not keep up. You work for an electrical services firm that this company contacted for help. They want a diagnosis and treatment plan they can implement over the winter. Your boss put you in charge of the troubleshooting.
The plant consists of four manufacturing buildings and an administrative building, all of which experienced issues. The HVAC system uses roof-mounted chillers and there are 32 of them in total. Six of these needed a motor replacement last year, and when you investigated further you found the plant replaces at least a couple of chiller motors each year.
What are some issues you should investigate?
The first issue to look at is not even electrical. If the units cannot keep up and motors are burning up, that's a sign of excessive load. A primary cause in these kinds of systems is a unit/roof-curb mismatch; bring in an expert to verify the units and ductwork match and the ductwork doesn't leak.
Next, look at the motor failures of the plant air system. If the rate is also high, then you probably have plant-wide problems with power quality, bonding deficiencies, motor maintenance, or any combination thereof. If the rate is low, that's a good indicator these issues are not plant-wide; focus your investigation for them on the HVAC system.
Try to find any evidence that condenser coils were icing up. A big clue that they probably were is the existence of easily accessible thermostats. If non-maintenance employees lowered thermostat settings, this would explain the icing and motor burnout.
Mark LamendolaMark Lamendola
Related
Dreamstime M 189308309
Indoor Ventilation Grid