Check Bonding Connections
Bonding connections are often overlooked in maintenance programs. Many maintenance electricians are confused as to what a bonding connection is, and that is partly due to language issues in the trade.
We see, for example, a “grounding” bus, lug, bar, or terminal in an equipment enclosure. However, it is actually a bonding connection. A grounding connection is a connection to earth (NEC Art. 100 definition). When you bond, you create a low-impedance path back to the source; it’s completely metallic, no dirt involved. The equipment grounding conductor is really a bonding conductor network, even though it ultimately connects to ground at the power source.
Simply put, you ground on the supply side of the service or separately derived source. You bond on the load side.
Those bonding connections are critical for protecting people and equipment from dangerous differences of potential and for overload protection and ground fault protection devices to work properly.
Over time, those connections loosen and/or corrode. A good maintenance program includes testing and inspection of all “grounding” (bonding) connections.
Mark LamendolaMark Lamendola