Unsafe Conditions in Start-Up Testing and Commissioning — Part 5
Before setting up in a particular area, do a walk-through to look for “structural” safety hazards. The following are three commonly encountered ones:
- Grounding and bonding errors. If you see a ground rod driven next to a piece of utilization equipment, stop immediately. Someone probably installed a path to the earth instead of creating a low-impedance metallic path back to the source. Metallic objects here probably have dangerous differences of potential. This must be resolved before any testing is performed.
- Inadequate clearances. You’re standing in front of a panel and see it’s only 3 ft to the yellow line behind you. Yet per the OSHA and the NEC tables, this panel requires 4-ft minimum clearance. Based on testing needs, it looks like another 4 in. to 6 in. will be needed.
- Miscellaneous NEC violations. Look for violations like raceway used as a support means, unused enclosure fittings that are still open, and even unequally sized conductors run in parallel as part of the same feeder circuit.