When the NEC talks about “wireway,” it is referring to a specific type of raceway. Wireways come in two types:
- Metal. These are sheet metal troughs with hinged or removable covers. They house and protect wires and cables, which are laid in the wireway after it is assembled as a complete system.
- Nonmetallic. These are the same as metal ones except they aren’t metal. They are, however, made from a flame-retardant material.
Obviously, the nonmetallic wireway can’t be used as an equipment grounding conductor (EGC). But can a metal wireway be used as an EGC? Section 250.118 lists types of EGCs. There 14 types listed. Wireway isn’t among them. But would number thirteen, “Other electrically continuous metal raceways and listed auxiliary gutters” include these? We can look more closely a these by turning to Article 376 (the nonmetallic ones are covered by Art. 378).
We don’t see anything under “Uses Permitted” [Sec. 376.10] or “Uses Not Permitted” [Sec. 376.12]. However, we find under “Grounding” [Sec. 376.60] you can use listed metal wireway an EGC. It does, in fact, make an excellent EGC because if its cross-sectional area. However, you should make any bonding connections to the body of the wireway not to any hinged or removable covers.
Note also, it must be a listed wireway. Custom-fabricated sheet metal ones may actually function just fine as EGCs, but they are not listed for this purpose and so cannot be used as EGCs.
About the Author
Mark LamendolaMark Lamendola
Mark is an expert in maintenance management, having racked up an impressive track record during his time working in the field. He also has extensive knowledge of, and practical expertise with, the National Electrical Code (NEC). Through his consulting business, he provides articles and training materials on electrical topics, specializing in making difficult subjects easy to understand and focusing on the practical aspects of electrical work.
Prior to starting his own business, Mark served as the Technical Editor on EC&M for six years, worked three years in nuclear maintenance, six years as a contract project engineer/project manager, three years as a systems engineer, and three years in plant maintenance management.
Mark earned an AAS degree from Rock Valley College, a BSEET from Columbia Pacific University, and an MBA from Lake Erie College. He’s also completed several related certifications over the years and even was formerly licensed as a Master Electrician. He is a Senior Member of the IEEE and past Chairman of the Kansas City Chapters of both the IEEE and the IEEE Computer Society. Mark also served as the program director for, a board member of, and webmaster of, the Midwest Chapter of the 7x24 Exchange. He has also held memberships with the following organizations: NETA, NFPA, International Association of Webmasters, and Institute of Certified Professional Managers.
Related
q and a on keyboard
q and a arrow on keyboard