NEC Rules for Induction and Dielectric Heating Equipment
How induction heating differs from dielectric heating
June 4, 2019
Article 665 provides the requirements for this equipment in industrial and scientific applications, including equipment used for melting and welding. Don’t confuse it with other types of heating equipment, such as types covered in Arts. 424, 425, 426, and 427 (all are in Chapter 4 Equipment for General Use).
How does induction heating differ from dielectric heating?
  • Induction: Heat is generated in a nominally conductive material due to its own I2R losses. Note that I2R means if you double the current, you quadruple the power loss.
  • Dielectric: Heat is generated in a nominally conductive material due to its dielectric losses when it’s placed in a varying electromagnetic field.
Two highlights:
  • You can determine the ampacity of the supply conductors by using the nameplate rating, unless those conductors supply motor-generator equipment. In that case, determine the supply conductor size per Art. 430, Part II [Sec. 665.10].
  • The rating disconnecting means must be at least the nameplate rating of the heating equipment. Motor-generator circuits must comply with Art. 430, Part IX.