Dacian_G/iStock/Thinkstock
Ecmweb 6897 Hot

When the Motor Runs Hot, Part 1

Dec. 9, 2014
Two options to consider when the temperature is out of spec.

Following your repair procedure, you use your handy infrared gun to measure temperatures at various points on the motor. Your repair procedure lists a high limit of 135°C for motors of this insulation class. But you read 152°C. The procedure doesn’t state what to do when the temperature is out of spec.

Should you replace this motor?

Maybe, because internal motor issues could be causing this high heat. But so could external motor issues. Here are two options to consider:

  • Voltage imbalance. This is the usual culprit. If the difference between any two phases is more than 2% of the nominal voltage, you have excessive voltage imbalance. The typical cause is improper allocation of single-phase loads. Lighting is a prime suspect, so look there first.
  • High ambient temperature. You may be able to solve this by improving air flow around the motor. It might be necessary to add ducting and even an electric fan. If the motor already has ducted cooling, check the air filter. It might just be clogged.

We’ll look at a few more options in Part 2.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

Considerations for Direct Burial Conduit

Installation type plays a key role in the type of conduit selected for electrical systems in industrial construction projects. Above ground, below ground, direct buried, encased...

Champion Strut Catalog

Champion Fiberglass is the most advanced manufacturing facility of fiberglass conduit, fiberglass bridge drain and fiberglass strut systems in the world. Its well-trained and ...