Q. Can a single transfer switch be used to supply both emergency and non-emergency loads, such as a UPS for telecom equipment?
A. No, a single transfer switch is not permitted to serve emergency and non-emergency loads [700.6(D)]. However, a single generator is permitted to serve emergency and non-emergency loads, provided multiple transfer switches are used, and automatic load shedding ensures adequate power for the emergency loads [700.5(B)] (Figure below).
The building feeder disconnecting means is permitted to be locked closed if there is concern that the opening of the readily accessible disconnect could result in a hazard to persons or property, lets say because of vandals or terrorism.
Got a Code question for Mike? Send it to him at [email protected].
Mike HoltMike Holt