• What's Wrong Here?
    Hint: This is a "hot" receptacle in more ways than one.
    Oct. 22, 2004
    Barry P., a member of the Electrical Contractor Network online community, found this installation in a plant somewhere in New York. As you can see from the glow of the volt-stick, the outlet is powered. Romex enters the back of the heater housing and is wired directly to the duplex receptacle. When it rains, water seeps under the wall, as this baseboard is located on an exterior wall.
    Per 110.11, “Unless identified for use in the operating environment, no conductors or equipment shall be located in damp or wet locations; where exposed to gases, fumes, vapors, liquids, or other agents that have a deteriorating effect on the conductors or equipment; or where exposed to excessive temperatures.
    “FPN No. 1: See 300.6 for protection against corrosion.
    “Equipment identified only as “dry locations,” “Type 1,” or “indoor use only” shall be protected against permanent damage from the weather during building construction.”
    We should also take note of 110.12, which states “Electrical equipment shall be installed in a neat and workmanlike manner.”
    Joe Tedesco