Code Quiz: Sizing of Grounded Conductor
NEC Rules for Sizing Grounded Conductors
Fill in the blank. When sizing a grounded conductor (installed in a single raceway) for a service-supplied alternating current system with a grounded conductor at the service point, the grounded conductor shall not be smaller than the required __________ conductor but shall not be required to be larger than __________. This system is operating over 1,000V.
A) grounding electrode / largest ungrounded service-entrance conductor(s)
B) main bonding jumper / supply-side bonding jumper
C) system bonding jumper / main bonding jumper
D) equipment grounding / intersystem bonding jumper
Scroll Down to See the Answer
Answer: A
As outlined in Sec. 250.186(A)(1), when sizing a grounded conductor (installed in a single raceway) for a service-supplied alternating current system with a grounded conductor at the service point, the grounded conductor shall not be smaller than the required grounding electrode conductor but shall not be required to be larger than the largest ungrounded service-entrance conductor(s).