NEC Requirements in Motor Fuel Dispensing Facilities
Article 514 of the National Electrical Code (NEC) provides the requirements for motor fuel dispensing facilities. Here are some highlights from this area of the Code:
- The requirements apply to locations where Class I [Art. 500] liquids are stored, handled, or dispensed [Sec. 514.3(B)].
- Figures 514.3(A) and (B) are graphics that helps you understand how areas are classified when adjacent to dispensers.
- Table 514.3(B)(1) is a large table that tells you the extent of the classified location based on its type of location and Division (Group D) or Zone (Group IIA). For example, for an outdoor remote pump that’s Division 1 the classified location is the entire space within any pit or box below grade level (if any part of the pit or box is within 10 ft horizontally from any edge of the pump). But for Division 2, the classified location is only 3 ft from any edge of the pump (extending horizontally in all directions).
- Table 514.3(B)(2) is a small table pertaining to compressed natural gas (CNG), liquified natural gas (LNG), or liquified petroleum gas (LP-Gas).
- New with the 2017 Edition of the NEC, Sec. 514.11 brings requirements for emergency disconnects.
- Grounding and bonding must comply with Sec. 501.30 [514.16].
Mark LamendolaMark Lamendola