The NEC and Art. 725: Circuits — Part 3
Part III of Art. 725 covers Class 2 and Class 3 circuits. Each is that portion of the circuit between a Class 2 or Class 3 power source and the connected load. What are these power sources?
- A listed Class 2 or Class 3 transformer.
- A listed Class 2 or Class 3 power supply.
- Other listed equipment marked to identify the Class 2 or Class 3 power source.
You can look at the power source characteristics in Chapter 9. Table 11(A) is for AC circuits, and Table 11(B) is for DC circuits. These tables and their associated notes take up a full page.
Highlights include:
- You can’t parallel the outputs of Class 2 or Class 3 power sources unless they are listed for that interconnection [725.121(B)].
- Install supply-side conductors per the applicable requirements of Chapters 1 through 4 [725.127].
- Choose load-side conductors that meet the application, as laid out in 725.179 and Table 725.179(J). For example, use CL2P for Class 2 plenum applications and CL3R for Class 3 riser applications [725.130(B)].