Understanding General Requirements of the NEC, Part 17
Article 110 provides general requirements for all installations. While Part II provides the requirements for systems operating at or below 1,000VAC or 1500VDC (nominal), Part III provides the requirements for systems operating over 1,000VAC or 1500VDC (nominal).
Some parts of Part III have changed with the 2026 revision to the NEC. One of those changes is the title now includes “1500 Volts dc”. This stating of both the AC and DC voltages is a general change throughout the NEC with the 2026 revision.
Where Part II systems tend to have enclosures you walk up to, Part III systems tend to have enclosures and vaults you walk (or crawl) into. Thus, the second section (Sec. 110.31) of Part III is about electrical installations that are “in a vault, room, or closet or in an area surrounded by a wall, screen, or fence.” The gist of it is that such a space “is considered to be accessible to qualified persons only.”
The differences between Part II and Part III are further illustrated in the requirements for indoor installations and outdoor installations. For Part II installations, there’s no mention of unqualified persons. In Part III, there is.
For Part III indoor installations that are accessible to:
- Unqualified persons, the equipment must be metal-enclosed [Sec. 110.31(B)(1)]. There are also requirements for marking and for diverting foreign objects away from energized parts if said objects are inserted through ventilation (or similar) openings.
- Qualified persons only, they must comply with Sec. 110.34 (workspace and guarding), Section 110.36 (circuit conductors), and Sec. 495.24 (minimum space separation) [Sec. 110.31(B)(2)].
For Part III outdoor installations that are accessible to:
- Unqualified persons, they must comply with Art. 267 Part I [Sec. 110.31(C)(1)]. Article 267 provides the requirements for branch circuits and feeders over 1000VAC, 1500VDC, nominal.
- Qualified persons only, they must meet the same requirements put forth for indoor installations [Sec. 110.31(C)(2). This subsection further stipulates these must comply with the first paragraph of Sec. 110.31 which means any enclosures used must be designed and constructed per the “nature and degree of the hazards associated with the installation.”
Table 110.31 provides the minimum distance from the fence to live parts, broken down by three nominal voltage ranges:
- 1001VAC to 13,700VAC or 1501VAC to 13700VDC, 10 ft.
- 13,800VAC or VDC to 230,000VAC or VDC, 15 ft.
- Over 230,000VAC or VDC, 18 ft.
Working space requirements for Part III equipment installations necessarily exceed those for Part II equipment installations. You will find the enhanced distances described in Sec. 110.32 Work Space About Equipment and Sec. 110.34(A) Working Space. Table 110.34(A) provides the minimum depth of working space at electrical equipment, and this is broken down into 5 voltage ranges.
Mark LamendolaMark Lamendola