Article 682 of the National Electrical Code (NEC) provides the requirements for electrical installations in and adjacent to bodies of water, whether natural or artificially made. Part II provides the bonding and grounding requirements. Some highlights from Part I:
- The equipotential plane is where conductive elements on, embedded in, or placed under the walk surface (within 3 in.), are bonded to all metal structures and equipment that may become energized [Sec. 682.2].
 - In land areas, the electrical datum plane (EDP) is two feet above “high water” [Sec. 680.2].
 - On floating structures, the EDP is 30 inches above water level (at the floating structure or landing stage) and 12 in. above the level of the deck [Sec. 680.2].
 - Unless a given piece of electrical equipment is identified for operation while submerged, no part of it can be below the EDP [Sec. 682.10].
 - Unless intended for operation while submerged, electrical connections cannot be below the EDP [Sec. 682.11].
 - If you install a 15A or 20A,125V receptacle in the datum plane, it must be GFCI-protected and the GFCI protection device must be at least 12 in. above the established EDP [Sec. 682.15].
