Q. Is an equipment grounding conductor always required in a PVC raceway between the electric utility meter and service disconnect?
A. Typically, an equipment grounding conductor is required in PVC, and when that is the case, a separate equipment grounding conductor of the wire type must be installed within the conduit [300.2(B) and 352.60]. However, there is an exception that deals with service raceways.
Exception No. 2: An equipment grounding conductor isn’t required in PVC conduit if the neutral conductor is used to ground service equipment, as permitted in 250.142(A) [250.24(C)].