Code Q&A: Securing and Supporting PVC Raceway
NEC rules for securing and supporting PVC raceways
Q. What is the Code rule for the securing and supporting of PVC raceways? Answer based on 2011 NEC.
A. PVC conduit must be securely fastened and supported in accordance with the following [352.30]:
• PVC conduit must be secured within 3 ft of every box, cabinet, or termination fitting, such as a conduit body [352.30(A)].
• PVC conduit must be supported at intervals not exceeding the values in Table 352.30, and the raceway must be fastened in a manner that permits movement from thermal expansion or contraction.
• PVC conduit installed horizontally in bored or punched holes in wood or metal framing members, or notches in wooden members, is considered supported, but the raceway must be secured within 3 ft of termination [352.30(B)].
Mike Holt