Code Q&A: Motor Protection
NEC rules for ptotecing motors against overload, short circuit, and ground fault by a single overcurrent device
Q. Does the Code allow a single overcurrent device to provide overload, short circuit, and ground fault protection for a motor? Can you also show me an example of how to size it? (Answer based on 2011 NEC.)
A. A motor can be protected against overload, short circuit, and ground fault by a single overcurrent device sized to the overload requirements contained in Sec. 430.32 [430.55].
Here’s a sample calculation:
What size dual-element fuse is permitted to protect a 5-hp, 230V, single-phase motor with a service factor of 1.15 and a nameplate current rating of 28A?
As per 430.32(A)(1), a motor marked with service factor of 1.15 or greater requires you to size the device at 125% of its full load current rating.
Therefore, 28A x 1.25 = 35A
Mike Holt
Mike Holt