Code Q&A: Sizing an Equipment Bonding Jumper
NEC rules for sizing an equipment bonding jumper sized for parallel feeder circuits in a cable
Q. What are the rules for sizing an equipment bonding jumper sized for parallel feeder circuits in a cable?
A. Bonding jumpers on the load side of feeder and branch circuit overcurrent devices are sized in accordance with Sec. 250.122, based on the rating of the circuit overcurrent device [250.102(D)]. For example, let’s say you’re installing parallel cables that are protected by a 1,200A overcurrent device. A quick check of Table 250.122 reveals the minimum size bonding jumper needed is 3/0 AWG. Each parallel cable must contain a full size equipment grounding jumper based on Table 250.122 [250.122(F)].
Mike Holt
Mike Holt