Code Q&A: Motor Controller Ratings
NEC requirements for motor controllers
Q. What is the Code requirement for the rating of a motor controller?
A. The controller must have one of the following ratings [430.83(A)]:
1) Horsepower rating — controllers, other than circuit breakers and molded-case switches, must have a horsepower rating not less than that of the motor.
2) Circuit breakers — a circuit breaker can serve as a motor controller [430.111]. Note: Circuit breakers aren’t required to be horsepower rated.
3) Molded-case switch — a molded-case switch, rated in amperes, can serve as a motor controller. Note: A molded-case switch isn’t required to be horsepower rated.
As noted in Sec. 430.83(C)(2), for stationary motors rated at 2 hp or less, the controller can be a general-use alternating-current snap switch, where the motor full-load current rating isn’t more than 80% of the ampere rating of the switch. Note: A general-use snap switch is a general-use switch constructed for installation in device boxes or on box covers [Art. 100].