Q. What is the minimum size requirement for branch circuit overcurrent protection?
Find the Answer
A. Branch-circuit overcurrent devices must have a rating of not less than 125% of the continuous loads, plus 100% of the noncontinuous loads [210.20(A)]. Note: See Sec. 210.19(A)(1) for branch-circuit conductor sizing requirements.
Exception: If the assembly and the overcurrent devices are both listed for operation at 100% of their rating, the branch-circuit overcurrent device can be sized at 100% of the continuous load.
It’s important to note that equipment suitable for 100% continuous loading is rarely available in ratings under 400A.
As noted in Sec. 210.20(B), branch-circuit conductors must be protected against overcurrent in accordance with 240.4. In addition, as noted in Sec. 210.20(C), branch-circuit equipment must be protected in accordance with 240.3.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visitwww.mikeholt.com/code.