Courtesy of www.MikeHolt.com
Based on the 2020 NEC.
Q. What are the Code rules relating to the protection of nonmetallic-sheathed cable and electrical nonmetallic tubing through metal framing members?
See answer below.
A. If Type NM cables pass through factory or field-made openings in metal framing members, the cable must be protected by listed bushings or listed grommets that cover all metal edges. The protection fitting must be securely fastened in the opening before the installation of the cable [Sec. 300.4(B)(1)].
If nails or screws are likely to penetrate Type NM cable or electrical nonmetallic tubing, a steel sleeve, steel plate, or steel clip not less than 1⁄16 in. in thickness must be installed to protect the cable or tubing [Sec. 300.4(B)(2)].
Exception: A listed and marked steel plate less than 1⁄16 in. thick that provides equal or better protection against nail or screw penetration is permitted.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.
Mike HoltMike Holt