Code Quiz: Torque Requirements
NEC rules on torque requirements for control circuit devices with screw-type pressure terminals used with 14 AWG or smaller copper conductors
What are the torque requirements for control circuit devices with screw-type pressure terminals used with 14 AWG or smaller copper conductors?
A. Come on! No one torques control circuit terminals.
B. Torque to a maximum of 12 lb-in.
C. Torque to a maximum of 7 lb-in.
D. Torque to a minimum of 7 lb-in., unless identified for a different torque value
Answer: D
Article 430 covers motors, motor circuits and controllers. Section 430.9 lists the requirements for terminals. More specifically, 430.9(C) states "Control circuit devices with screw-type pressure terminals used with 14 AWG or smaller copper conductors shall be torque to a minimum of 7 lb-in. unless identified for a different torque value."