Code Quiz: Underground Systems Containing Mixed Wiring Types
Fill in the blank with the appropriate answer.
Per Sec. 820.47(A) of the 2014 NEC, when installing underground coaxial cables in a duct, pedestal, handhole enclosure, or manhole that contains electric light, power, or Class 1 or non-power-limited fire alarm circuit, conductors shall be in a section permanently separated from such conductors by means of a _________.
A) suitable barrier
B) rigid metal conduit
C) intermediate metal conduit
D) rigid polyvinyl chloride conduit
Answer: A
Article 820 covers coaxial cable system installations. As noted in Sec. 820.47(A), when installing underground coaxial cables in a duct, pedestal, handhole enclosure, or manhole that contains electric light, power, or Class 1 or non-power-limited fire alarm circuit, conductors shall be in a section permanently separated from such conductors by means of a suitable barrier.
Owen is the owner and president of National Code Seminars and the holder of master electrician certifications in 46 states. He can be reached at [email protected].