Code Quiz: Permitted Voltage Ratings for Class 2 and Class 3 Cables
March 17, 2016
Fill in the blank with the appropriate answer.
When are the voltage ratings permitted on Class 2 and Class 3 cables, per the listing requirements of Part IV of Art. 725?
A) Not permitted
B) When the cable rating exceeds 600V
C) Where the cable has multiple listings and a voltage marking is required for one or more of the listings
D) None of the above
Answer: C
As noted in Sec. 725.179(K), cables shall be marked in accordance with 310.120(A)(2)-(5), and Table 725.179(K).
Exception: Where the cable has multiple listings and a voltage marking is required for one or more of the listings.